Sinumerik Alarm 380003 Profibus-DP: operating error, reason %1,parameter %2 %3 %4.
%1 = Cause of the error
%2 = Parameter 1
%3 = Parameter 2
%4 = Parameter 3
An operating error occurred on the PROFIBUS DP in cyclic mode. Overview: Cause of the error, Par 1, Par 2, Par 3:
• 01 = unknown alarm, Alarm class, Logical address, —
• 02 = DPM cycle timeout, DPM actual value status, DPM setpoint value status, —
• 03 = DPM cycle status, DPM actual value status, DPM setpoint value status, DPM error code
• 04 = DPM cycle error, DPM actual value status, DPM setpoint value status, DPM error code
• 05 = client not registered, Client number, Max. number of clients, —
• 06 = synchronization error, Number of sync violation, –, — Alarm class: (see alarm 380060) The following can be primary causes:
• For error cause 01: Data transfer error on PROFIBUS DP
• For error cause 02, 03, 04: Error in contents of SDB1000
• For error cause 02, 03, 04, 05: Corruption of parts of system program
• For error cause 06: The PCI bus cycle does not match the expected rate and synchronization is not possible for this reason. The correct PCI bus cycle must be entered. The error can also be caused by a hardware problem on the MCI module.
• Check the electrical and fault-related specifications for PROFIBUS DP, assess the cable installation
• Check the terminating resistors of the PROFIBUS connectors (ON setting at end of cable, otherwise OFF setting required)
• Check slave
• Check SDB1000
• Follow the procedure described for troubleshooting alarm 380 001
• The correct PCI bus cycle must be entered. If the error cannot be eliminated by this procedure, please make a note of the error text and contact the control system manufacturer.