Sinumerik Alarm 300769 Axis %1 drive %2 denominator bandwidth > double natural frequency
Parameters:
%1 = NC axis number
%2 = Drive number
Definitions:
The bandwidth denominator of a current or speed setpoint filter is greater than twice the natural frequency. This error message is only issued for the general bandstop filter if:
• Speed setpoint filter 1:
• MD 1516 > 0.0 or
• MD 1520 <> 100.0
• Speed setpoint filter 2:
• MD 1519 > 0.0 or
• MD 1521 <> 100.0
• Current setpoint filter 1:
• MD 1212 > 0.0
• Current setpoint filter 2:
• MD 1215 > 0.0
• Current setpoint filter 3:
• MD 1218 > 0.0
• Current setpoint filter 4:
• MD 1221 > 0.0
The alarm can be reprogrammed in the MD ALARM_REACTION_CHAN_NOREADY (channel not ready).
Reactions:
– NC not ready.
– Channel not ready.
– NC Stop on alarm.
– NC Start disable in this channel.
– The NC switches to follow-up mode.
– Alarm display.
– Interface signals are set.
Remedy:
Please inform the authorized personnel/service department. The bandwidth denominator of a current or speed setpoint filter must be less than twice the natural frequency.
• MD 1515 <= 2 * MD 1514 * 0.01 * MD 1520• Speed setpoint filter 2:• MD 1518 <= 2 * MD 1517 * 0.01 * MD 1521• Current setpoint filter 1:• MD 1211 <= 2 * MD 1210• Current setpoint filter 2:• MD 1214 <= 2 * MD 1213• Current setpoint filter 3:• MD 1217 <= 2 * MD 1216• Current setpoint filter 4:• MD 1220 <= 2 * MD 1219• Modify MD 1515: $MD_SPEED_FILTER_1_BANDWIDTH (bandwidth speed setpoint filter 1)• Modify MD 1514: $MD_SPEED_FILTER_1_SUPPR_FREQ (suppression frequency speed setpoint filter 1)• Modify MD 1520: $MD_SPEED_FILTER_1_BS_FREQ (bandstop filter natural frequency speed setpoint filter 1)• Modify MD 1518: $MD_SPEED_FILTER_2_BANDWIDTH (bandwidth speed setpoint filter 2)• Modify MD 1517: $MD_SPEED_FILTER_2_SUPPR_FREQ (suppression frequency speed setpoint filter 2)• Modify MD 1521: $MD_SPEED_FILTER_2_BS_FREQ (bandstop filter natural frequency speed setpoint filter 2)• Modify MD 1211: $MD_CURRENT_FILTER_1_BANDWIDTH (bandwidth current set- point filter 1)• Modify MD 1210: $MD_CURRENT_FILTER_1_SUPPR_FREQ (suppression frequency current setpoint filter 1)• Modify MD 1214: $MD_CURRENT_FILTER_2_BANDWIDTH (bandwidth speed set- point filter 2)• Modify MD 1213: $MD_CURRENT_FILTER_2_SUPPR_FREQ (suppression frequency current setpoint filter 2)• Modify MD 1217: $MD_CURRENT_FILTER_3_BANDWIDTH (bandwidth speed set- point filter 3)• Modify MD 1216: $MD_CURRENT_FILTER_3_SUPPR_FREQ (suppression frequency current setpoint filter 3)• Modify MD 1220: $MD_CURRENT_FILTER_4_BANDWIDTH (bandwidth speed set- point filter 4)• Modify MD 1219: $MD_CURRENT_FILTER_4_SUPPR_FREQ (suppression frequency current setpoint filter 4)Program Continuation:
Clear alarm with the RESET key in all channels. Restart part program.
References
  1. Siemens Diagnostics Guide by Siemens